Author Topic: Power required to run a reel / touch machine. ?  (Read 1341 times)

0 Members and 1 Guest are viewing this topic.

Offline Keats

  • New NLG Member 3 to 100 Posts
  • **
  • Posts: 75
  • Reputation Power: 6
  • Keats New User has no influence.
  • Gender: Male
  • NLG
Power required to run a reel / touch machine. ?
« on: March 21, 2023, 11:25:49 AM »
21 March 2023
I don't know where to find this info.

Does anyone know about how much power ( Amps ) is required to run my new Bucks Ahoy S2000 machine with a topper ?

I want to run the Bucks Ahoy machine and my IGT S + Model B5133 (made in 12/1993) on the same circuit. I have to assume that the S2000 Bucks Ahoy would use more power. It has a Topper and numerious florescent lamps. The older nickle machine is a pretty basic machine without a lot of extras.

Before I overload the 15 amp GFCI breaker, I'd like to know how much juice they take together.

I have two other machines, a Game King and an S2000 (Triple Lucky 5 reel), that are running on a different 15 amp circuit at the same time now. (Not a GFCI circuit).

Perhaps there's a place that lists the required amperage and / or watts consumed?

I know that they are all 120 volt, so if I can get the amps or the watts I can figure out the other values.

Any thoughts would be appreciated.

Keats
Peoria, Az.



« Last Edit: March 24, 2023, 09:20:47 PM by qbert »

Offline jay

  • Global NLG Site Moderator
  • NLG Member 501 to 10,000 Posts
  • *
  • Posts: 2122
  • Reputation Power: 164
  • jay Is an-NLG GOD!jay Is an-NLG GOD!jay Is an-NLG GOD!jay Is an-NLG GOD!jay Is an-NLG GOD!jay Is an-NLG GOD!jay Is an-NLG GOD!jay Is an-NLG GOD!jay Is an-NLG GOD!jay Is an-NLG GOD!jay Is an-NLG GOD!jay Is an-NLG GOD!
  • Gender: Male
  • The only way to beat the casino is to own it.
Re: Power required to run a reel / touch machine. ?
« Reply #1 on: March 21, 2023, 11:43:56 AM »
The simple way to check is to pull the fuses on the machine. The largest which is likely not over 5amp would be your answer.
Generally speaking slots do not take a lot of power. They are a computer board and some florescent or LED lights....
On a S+ with a topper you have 4x 15w florescent tubes at best. This is less than 1 incandescent 60w bulb.

Your largest draw would be when the bill validator, hopper or printer is running. All have motors and draw more than the rest of the unit. This would be your 2-3amp draw.

When looking at your total draw - it is unlikely that 2 hoppers would be running concurrently

Your breaker is there for your protection. If you do accidently draw more than 15amps - which I don't believe its possible with just 2 slots. It will pop and cut off the power..... so the answer is really loader up and if it pops move to a second circuit.  No harm will come to your wiring or your machines.




If you can't afford to lose you can't afford to win.

If you find this site helpful, please consider making a small donation to help defray the cost of hosting and bandwidth.

Please do not PM me for support or "how to" requests -- please post your request in the forum so that everyone may assist you and everyone can benefit from the answer to your question!  Thanks! :)

Offline qbert

  • Topic Moderator
  • NLG Member 501 to 10,000 Posts
  • *
  • Posts: 2697
  • Reputation Power: 184
  • qbert Is an-NLG GOD!qbert Is an-NLG GOD!qbert Is an-NLG GOD!qbert Is an-NLG GOD!qbert Is an-NLG GOD!qbert Is an-NLG GOD!qbert Is an-NLG GOD!qbert Is an-NLG GOD!qbert Is an-NLG GOD!qbert Is an-NLG GOD!qbert Is an-NLG GOD!qbert Is an-NLG GOD!
  • Gender: Male
  • NLG
Re: Power required to run a reel / touch machine. ?
« Reply #2 on: March 21, 2023, 04:45:47 PM »
Fully loaded Reel Touch with standard fluorescent lights runs between 260-275 watts
If you find this site helpful, please consider making a small donation to help defray the cost of hosting and bandwidth.

Offline Keats

  • New NLG Member 3 to 100 Posts
  • **
  • Posts: 75
  • Reputation Power: 6
  • Keats New User has no influence.
  • Gender: Male
  • NLG
Re: Power required to run a reel / touch machine. ?
« Reply #3 on: March 21, 2023, 04:48:18 PM »
21 Mar 23
Jay,

Thank you. after searching all over the net, I found a place that showed some info for an older machine.
It listed the draw as:
Adv Idle 180 watts / 115 VAC = 1.5 Amps
Worst case 400 watts / 115 VAC = 3.7 Amps.
So if each machine was in the Worst case state it would be 3.7 X 2 = 7.4 Amps.

That should probably cover the electrical demand for the florescent lamps turned on and everything running at the same time.

There are no hoppers involved on the Game King. So only my older S+ nickle machine could be making a coin pay out. I've already disabled the Cash Out button on that machine. I didn't want guests to cash out any coins. Easier to just keep a bowl of nickles next to the machine if they insist on using coins to play. It does take bills so there's really no need to even do that.

When I get these machines running on the 20 Amp circuit, I'll do another posting with the results.

Thanks again,
Keats
Peoria, Az.

Offline Keats

  • New NLG Member 3 to 100 Posts
  • **
  • Posts: 75
  • Reputation Power: 6
  • Keats New User has no influence.
  • Gender: Male
  • NLG
Re: Power required to run a reel / touch machine. ?
« Reply #4 on: March 21, 2023, 04:53:02 PM »
Fully loaded Reel Touch with standard fluorescent lights runs between 260-275 watts
-------------------------
Thanks.
Watts divided by volts equals amps. If I'm correct...
So 260 divided by 115 volts = 2.26 Amps.
and 275 divided by 115 volts = 2.39 amps.

I'm thinking that the two machines together might reach 5 amps worst case. Should fit well in the 20 amp limit of the breaker.

Thanks again

Keats
Peoria, Az.

Offline jay

  • Global NLG Site Moderator
  • NLG Member 501 to 10,000 Posts
  • *
  • Posts: 2122
  • Reputation Power: 164
  • jay Is an-NLG GOD!jay Is an-NLG GOD!jay Is an-NLG GOD!jay Is an-NLG GOD!jay Is an-NLG GOD!jay Is an-NLG GOD!jay Is an-NLG GOD!jay Is an-NLG GOD!jay Is an-NLG GOD!jay Is an-NLG GOD!jay Is an-NLG GOD!jay Is an-NLG GOD!
  • Gender: Male
  • The only way to beat the casino is to own it.
Re: Power required to run a reel / touch machine. ?
« Reply #5 on: March 21, 2023, 05:27:19 PM »
I think your being overly conservative.
I am running 3 S+ and a PE+ along with a couple of Neon signs off a 15amp breaker, never had an issue.
My Pinball and the rest of the neon are on a second breaker.

The typical household is wired with what is called 14/2 wire. 14gage 2 conductors + a ground wire.
If you change your breaker from a 15a to a 20a you should also be changing your wiring from 14/2 to 12/2.
Thicker wire to compensate for the potential for a higher draw. The plugs are also different. They look like a regular duplex but have a L-shaped slot for high draw equipment.
The screw terminals are also longer on these plugs to allow them to be opened wider for the thicker wire. You are not to use regular plugs for 12/2 wire.

Not that I have ever seen it happen but theoretically 14/2 loaded with 20a of power can spontaneously erupt in flames and is not legal.
If you can't afford to lose you can't afford to win.

If you find this site helpful, please consider making a small donation to help defray the cost of hosting and bandwidth.

Please do not PM me for support or "how to" requests -- please post your request in the forum so that everyone may assist you and everyone can benefit from the answer to your question!  Thanks! :)

Offline Keats

  • New NLG Member 3 to 100 Posts
  • **
  • Posts: 75
  • Reputation Power: 6
  • Keats New User has no influence.
  • Gender: Male
  • NLG
Re: Power required to run a reel / touch machine. ?
« Reply #6 on: March 22, 2023, 09:16:58 AM »
I think your being overly conservative.
I am running 3 S+ and a PE+ along with a couple of Neon signs off a 15amp breaker, never had an issue.
My Pinball and the rest of the neon are on a second breaker.

The typical household is wired with what is called 14/2 wire. 14gage 2 conductors + a ground wire.
If you change your breaker from a 15a to a 20a you should also be changing your wiring from 14/2 to 12/2.
Thicker wire to compensate for the potential for a higher draw. The plugs are also different. They look like a regular duplex but have a L-shaped slot for high draw equipment.
The screw terminals are also longer on these plugs to allow them to be opened wider for the thicker wire. You are not to use regular plugs for 12/2 wire.

Not that I have ever seen it happen but theoretically 14/2 loaded with 20a of power can spontaneously erupt in flames and is not legal.
_____________________________________________________
The circuit is already 20 amps. That's the way the house was wired when built in 2000. I'm pretty sure that the builder used 12/2 wire. I can pull the socket and check it just to be sure.
Thanks

Keats
Peoria, Az.

 

Cell Phone and Pad Mode

imode wap wap2

NLG Archives

Archives @ newlifegames.net Wayback Machine

Contact Us

NLG Shop 928 754-4147 Email Us 1788 Highway 95 30 BHC City AZ 86442
If you find this site helpful, please consider becoming a Contributing NLG Member with a monthly subscription to help cover the cost of pizza, coffee, aspirin, hosting, and bandwidth.
Contributing Members: get unlimited personal messages, can save topics and replies as drafts,
can post to the Classified ads, get unlimited access to the downloads, and also get this minty badge:



**Subscription Link** (Click Here) **Subscription Link**



           
If you would rather remain anonymous Thank You or just want to help support the site, please use this "make a donation" button:




From your entire NLG staff, thank you for supporting NLG.


New Life Games LLC 1788 HIGHWAY 95 UNIT 30 BULLHEAD CITY AZ 86442




Newlifegames.com     Newlifegames.net     Newlifegames.org

Newlifegame.com     Newlifegame.net     Newlifegame.org    Newlifegames.us

   New Life Games     NewLifeGames  NLG

 We Bring new Life to old Games    1-888-NLG-SLOTS

Are all Copyright and Trademarks of New Life Games LLC 1992 - 2022


FAIR USE NOTICE:



This site contains copyrighted material the use of which has not always been specifically authorized by the copyright owner.
We make such material available in an effort to advance awareness and understanding of the issues involved.
We believe this constitutes a fair use of any such copyrighted material as provided for in section 107 of the US Copyright Law.
In accordance with Title 17 U.S.C. Section 107, the material on this site is distributed without profit to those
who have expressed a prior interest in receiving the included information for research and educational purposes.

For more information please visit: http://www.law.cornell.edu/uscode/17/107.shtml
If you wish to use copyrighted material from this site for purposes of your own that go beyond fair use,
you must obtain permission directly from the copyright owner.




The NewLifeGames.com website is optimized for use with Firefox and a minimum screen resolution of 1600 x 900 pixels.

SimplePortal 2.3.5 © 2008-2012, SimplePortal